Mike,
Back at post 8 you posted a circuit based on 5 logic IC's and had in a few posts prior to that stated it was working.
The description and circuit generally corresponds to the diagram from another forums post as per attached.
Yet with three pairs of probes in the one tank, I might think that there would be some capacitive (or other) coupling between the pairs of probes leading to difficulties in control and sensing.
The image of the tank in post 10 shows little sign of the probes or any already working circuit.
Exactly how much of the hardware have you constructed already ? Any photos of what has been done so far?
A method often used to sense liquid level in a tank involves only three probes in total:
- A common probe to the bottom of the tank
- A low level probe to a point near the bottom of the tank (or the level where the input supply is the start filling again), and
- A high level probe form the top to a high point (used to stop the water supply)
If the tank delivery line is drained (back flow or is there a check/non-return valve?) when the supply is stopped maybe some probe(s) in the supply pipe to detect presence of water/flow may suffice.
EDIT:
With the newer M2 series PICAXE chips, it may even be possible to use the TOUCH sensor input with the probes as contacts in the side of the tank for level sensing.
It can all depend upon the repeatability, purpose (home industrial), user requirements and ability to seal a side mounted contact plate on the plastic tank side.